So Thom, would the "no pump" calc only include the number of heads
from zero flow to 350 gpm noting that that many heads would operate
properly at 48 psi and then prove that the entire design area would
operate with the pump running?

On 4/1/07, Thom McMahon <[EMAIL PROTECTED]> wrote:
We have a municipal water system which operates at 48 psi most of the time, 
however when the flow exceeds 350 Gpm the fire pump kicks in and boosts the 
system to 145 Psi, @ 2000 gpm. Whenever a flow test is performed the results 
are always based upon the fire pump flow.
As we all know most fires are contained or extinguished by one to three heads. 
Obviously this isn't enough to make the fire pump kick in.
The local Fire Chief has started to question the operation of systems installed using the full flow 
of the fire pump, since even in flow conditions over 350 Gpm it can take as long as 2 (Two) minutes 
for the pump to kick in. The bigger concern as I see it is that the design for any system up to 350 
Gpm should be based upon "NO" fire pump, with two sets of calculations one for flow up to 
350, and another for flow over 350. This way we can be sure that the sprinkler heads will have the 
min. pressure and flow even if only a few go off. The other calc should be easy to prove, as over 
350 there will be a large increase in pressure available. The caveat is that the higher flow 
calculation cannot be used to reduce the pipe size below those used for the lower calc. It is just 
a "Proof" calc.

Does this sound like the right approach?
No the city has no intention of changing the pump set up any time soon.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to