Short answer YES.
Obviously for many light hazard occupancies, the "NO" fire pump calc would
have to be the entire system demand design, where as for systems where say a
500 Gpm demand is required, we would design up to say 400 Gpm of flow and
the appropriate number of heads flowing, to allow for the pump start delay,
and then just prove the 500 Gpm flow using the Fire Pump.
As a follow up question for you guy's that see a lot more fire pumps than we
do, What is an acceptable pump operation delay in most jurisdictions?
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Ron Greenman" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, April 02, 2007 9:37 AM
Subject: Re: Flow test & fire pump
So Thom, would the "no pump" calc only include the number of heads
from zero flow to 350 gpm noting that that many heads would operate
properly at 48 psi and then prove that the entire design area would
operate with the pump running?
On 4/1/07, Thom McMahon <[EMAIL PROTECTED]> wrote:
We have a municipal water system which operates at 48 psi most of the
time, however when the flow exceeds 350 Gpm the fire pump kicks in and
boosts the system to 145 Psi, @ 2000 gpm. Whenever a flow test is
performed the results are always based upon the fire pump flow.
As we all know most fires are contained or extinguished by one to three
heads. Obviously this isn't enough to make the fire pump kick in.
The local Fire Chief has started to question the operation of systems
installed using the full flow of the fire pump, since even in flow
conditions over 350 Gpm it can take as long as 2 (Two) minutes for the
pump to kick in. The bigger concern as I see it is that the design for
any system up to 350 Gpm should be based upon "NO" fire pump, with two
sets of calculations one for flow up to 350, and another for flow over
350. This way we can be sure that the sprinkler heads will have the min.
pressure and flow even if only a few go off. The other calc should be
easy to prove, as over 350 there will be a large increase in pressure
available. The caveat is that the higher flow calculation cannot be used
to reduce the pipe size below those used for the lower calc. It is just a
"Proof" calc.
Does this sound like the right approach?
No the city has no intention of changing the pump set up any time soon.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)