Cliff, You're doing what is required. Its not a matter of right or wrong. We go through this extensive consensus, public comment, advertised adoption process only to have the selective design and or enforcement often in blatant disregard for adopted codes and standards. Keep up the good work. PS, fishing sounds good but not because your frustrated.
John Drucker Fire Protection Subcode Official (AHJ) Red Bank, New Jersey -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Cliff Whitfield Sent: Tuesday, April 03, 2007 2:39 PM To: [email protected] Subject: RE: Elevator Inspectors vs. Piping Installation per NFPA I'm not trying to be difficult, (I don't think) but if NFPA 13 requires it, the only correct way to design it is with a head in the pit whether the AHJ or the EoR show it or require it. Unless the AHJ has some written variance that has been adopted. It is our responsibility as "layout technicians" to follow the code. Am I the only one on the forum that feels that way today? Maybe I should go fishing or something! Cliff -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Tuesday, April 03, 2007 1:07 PM To: [email protected] Subject: RE: Elevator Inspectors vs. Piping Installation per NFPA I guess I should have worded that a little better but it was almost lunch time and I was on my way out the door. The majority of the jobs we do the AHJ does not require a head in the pit for whatever reason. If the Engineer of Record does not call one out, and they rarely do, then we do not add one, I do agree though that if there is known combustible hydraulic fluid in the shaft a head should be installed. Regards, Brian Harris First Defense Fire Protection Design Engineer [EMAIL PROTECTED] 704.948.3506 phone 704.948.3507 fax -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Cliff Whitfield Sent: Tuesday, April 03, 2007 12:39 PM To: [email protected] Subject: RE: Elevator Inspectors vs. Piping Installation per NFPA Brian, I'm not sure where you get your info on this but NFPA 13 (02) 8.14.5.1 requires heads in the pit unless that pit meets the requirements of 8.14.5.2. As Chuck mentioned, nearly all of the hydraulic fluids used for non-cable operated elevators is combustible. You have to put them in to meet NFPA 13. What the GC does after that is his business but if he wants you to take it out, make sure you get written direction to do it and keep it in your files along with your letter of objection. Cliff -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Tuesday, April 03, 2007 11:12 AM To: [email protected] Subject: RE: Elevator Inspectors vs. Piping Installation per NFPA Chuck, It's 80 and sunny here in North Carolina...... Unless otherwise directed by the AHJ the rule of thumb is no sprinklers required in the pit, only in the machine room for hydraulic type elevators. Regards, Brian Harris First Defense Fire Protection Design Engineer [EMAIL PROTECTED] 704.948.3506 phone 704.948.3507 fax -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Haugen, Charles Sent: Tuesday, April 03, 2007 12:07 PM To: [email protected]; [EMAIL PROTECTED] Subject: Elevator Inspectors vs. Piping Installation per NFPA It's snowing again in Fargo! I know this has been asked before... I apologize. I have looked through NFPA 13, '99, '02, and '07 editions regarding protection in the pit... I've been on the phones w/ A.H.J.'s regarding their takes on protection... and the war that's waged w/ the Elevator inspector NOT wanting anything in the pit OR the elev. mech. room. When asking the elevator installers regarding if they're using 'noncombustible hydraulic fluids' we get the deer in the headlights look followed by a "...does that even exist?" comment. There has been a time or two where we have been instructed by the Elev. Inspector to remove all piping in these areas after the Fire Inspector has been through. What to do? I recall that there were talks about this during the NFPA meeting?? Correct? Chuck _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)