Travis,

NFPA 13 (2002) 3.3.4 defines ceiling height as the distance between the floor and roof deck. By your commentary, it looks like you would have to use the 28' height. If you had a waffle-type pattern, you might be able to make some justification since you would not likely have a ceiling jet above the bottom of the lowest point of the structure in that situation. Would it be practical to have them construct a ceiling at the bottom of the tees?



At 02:03 PM 4/9/2007, you wrote:
Ok..this may be a stupid question, but here goes:

If I have concrete tee construction, what can I use as the roof deck.  I
have an area with 28' to bottom of deck and 26'-2" to bottom of tee.  If I
can use the bottom of tee as the maximum ceiling height, then I can use 0.60
gpm  density using Tyco k17-231 sprinklers.  If I need to use 28', then the
density goes to 0.80 gpm / sq ft.  This is a retrofit, and the existing
system works with 0.60, but does not work with 0.80.  I am looking for
something to justify the 0.60 gpm as being adequate.

Travis Mack, SET
MFP Design, LLC
480-505-9271
[EMAIL PROTECTED]

Examine yourselves to see if your faith is genuine. Test yourselves. Surely
you know that Jesus Christ is among you; if not, you have failed the test of
genuine faith.  2 Corinthians 13:5 NLT

--
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.26/752 - Release Date: 4/8/2007
8:34 PM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to