Chris makes a more than valid point here regarding water supply and
manning issues.  In fact, the fire service continually debates manning
and related issues all the time...Heck despite the fact that I generally
agree with his premises... I could easily change the flow rates, number
of lines and staffing ratios and we would all be hard pressed to hit a
REAL answer.  

The truth is that the fire service is a human element service and there
are rules of thumb and they tend to stick around.....some even quip that
the fire service slogan should be "200 years of tradition unhindered by
progress."  Sadly this sometimes rings true.

Which brings me to the real point of my post....Where did the 500 gpm
for the first riser and 250 gpm for each additional riser (max 1000 gpm)
come from? 

Do we really need that much water?  Particularly in sprinklered low rise
buildings?  I can see the need in a high rise where stretching lines
from the street is not really possible...but do we really need it in a 3
story apartment building that is fully sprinklered?

Feel free to start the debate.  That is my intent by making this post.

Paul Sincaglia, P.E.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Cahill
Sent: Wednesday, April 11, 2007 9:28 AM
To: [email protected]
Subject: RE: Manual wet standpipes

This is theory vs. reality issue.  To flow 1000 gpm in a building either
the
FD needs to have 4-5 2-1/2" lines in operation or about 8-9 1-3/4".
Each
line takes 3-4 people to staff or one company.  So the optimistic case
with
the rare FD set up with 2-1/2" lines 4 companies on the lines, plus at
least
2 interior search and rescue, one outside to rescue FF if need be.  Now
we
need to add all their replacements for when they run out of air and for
them
to get rest.  So conservatively triple the number of working units to
keep 4
lines in operation.  And if you ever handled 2-1/2" hose under fire
condition really 2 companies per line is necessary if you actually try
to
advance the hose.  So IMHO 19 companies plus any logistical support is
the
minimum to sustain 1000 gpm in a building.  There are very, very few
places
that could do this, even with mutual aid. 

Then there is another discussion about where exactly do you put 1000
gpm.
If the fire is that big you got to start asking what are you doing
inside
the building.  

So theory is plan for 1000 gpm, reality is the human element can't or
shouldn't pull it off.  I'm sure someone will give an example of where
it
was done but these will be few and far between.  I'd limit guesses to
FDNY,
BFD, Philly, Houston, Dallas, Miami, LA, SFFD, Chicago and at best a few
other big cities.  Neither Minneapolis nor St. Paul IMHO could do it,
maybe
working together, maybe.  And they are like top 60 sized cities in the
US. 

I'll admit another bias of mine.  If the sprinklers don't control it or
the
first line doesn't get it the FD is just putting on a show for the
public.
Or at least with regards to the building of origin.  For you other FF
out
there how many times did you give yourselves a high five for a great
save
only to see the dozers the next day.        

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [EMAIL PROTECTED]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Wednesday, April 11, 2007 7:14 AM
To: [email protected]
Subject: RE: Manual wet standpipes

Along these same lines, why doesn't the code dictate FDC sizes based on
system demand? 

For instance if there is one FDC feeding 3 standpipes I believe that 14
should require a minimum of a 3 way FDC to eliminate confusion and
argument.

Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to