Bill,

My reasoning here is that the fire service main and the FDC are both
delivery lines to the system or part of the underground piping which
would be covered on the UG materials and installation form and subject
to the rules of NFPA 24, whereas the described situation is a part of
the system covered by the aboveground materials and installation form
and subject to the rules of NFPA 13. Ductile is not in 13-6.3 (2002).
I suppose that if you consider that in this situation you revert to 24
when you go back underground then D.I. would be acceptable.

On 4/19/07, Bill Minkel <[EMAIL PROTECTED]> wrote:
 When an FDC line goes underground it becomes D.I., I would think a Dry
System Main is no different.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Tuesday, April 17, 2007 7:08 PM
To: [email protected]
Subject: Re: Underground Dry Pipe

My opinion would be you cannot use ductile since, even though this pipe is
going to be underground, it is essentially a part of the aboveground system
and a dry system at that so you are restricted to approved pipe types. Of
course you don't want to directly bury steel pipe, galvanized or not, in
direct earth contact. I'd take a note from the gas fitters that used a
pre-wrapped or site-wrapped black steel pipe. There's a spec on how thick
the plastic is (10 mil I think) but that can be found in the UPC. As to low
point drain is your buried below the frost line you don't need to worry
about the pipe down there although I'd drain it anyways since you'll need to
drain the ends that are above that line. To do this I'd suggest a digging a
small, lined dry well (maybe 6" by 24" deep) wherever you're planning a
drain. Fill this with gravel. Bring a keyed valve (like the ones for lawn
sprinklers) to the well and surround it with a road box.

On 4/17/07, Margaret Zabel <[EMAIL PROTECTED]> wrote:
> Re:  my previous post about a dry standpipe installation, I believe
> that the large pipe was all standard-type underground pipe:  ductile
> iron as I recall.  The much smaller connection for the drain may have
> been handled with some specially lined 2" pipe for the drain.  There
> is a company in southern California somewhere (Santa Fe Springs?)
> which will cement-line steel pipe for you on a custom basis. I have
> used their services on government-only jobs in the past where function
> was more important than listing.  This job I am referring to was for
> the county in which the airport is located.  Since we needed only
> about 5' of small pipe, we may have done something else.  I don't
> remember.  (Guess I'd make a good politician....)
>
> Margaret Zabel
>
> --- Roland Huggins <[EMAIL PROTECTED]> wrote:
>
> > the use of underground steel pipe is restricted, see 10.1.2.  One
> > can argue about whether it applies just to supply mains (since it
> > came out of NFPA 24) since 8.16.4.2.4 addresses it.
> > Transitioning WITHIN
> > a sprinkler system (ie after the system riser), has never been well
> > defined.  Skate on out there on that thin (unknown) ice.
> >
> > Roland
> >
> > On Apr 17, 2007, at 2:05 PM, Reed Roisum wrote:
> >
> > > I've got a outdoor amphitheatre that needs
> > sprinkler protection.  The
> > > only option allowed to get from the controls
> > (adjacent heated
> > > building)
> > > to the arch on the amphitheatre is to go
> > underground.  We will be
> > > using
> > > galvanized pipe for the dry system for the
> > amphitheatre.
> > >
> > > The question is what pipe should I spec for the
> > dry underground?  Can
> > > (should) I use galvanized?  Do you sleeve it?  Any
> > other suggestions?
> > >
> > > Thanks,
> > >
> > >
> > > Reed Roisum
> > > Fire Protection Technician
> > >
> > > Ulteig Engineers, Inc.
> > > 3350 38th Avenue South
> > > Fargo, ND 58104-7079
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> >
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email to:Sprinklerforum-
> > > [EMAIL PROTECTED] (Put the word unsubscribe in the subject
> > > field)
> > >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to