NFPA 13 clearly states that we can not use 8.0 k heads with 1/2" threads in
new installations. I assume there are reasons for this but I do not know
them.

BUT, we have a new job with pipe on the floor and 1/2" welded outlets for
5.6 k sprinklers. The problem is we ran into some lights and are having to
move some pipe which blows our calcs. (Our designer made a mistake and did
not realize that the lights are not hanging, but are mounted to the
purlins.)

We had in excess of 10% cushion and now we have -5%. If we use the 8K heads
we are fine. 

The other option is to reorder all of the branchline piping 1 size larger.

We reflowed the hydrants to confirm the water and lost 10 psi residual to
make matters worse.

Does anyone on the committee have any input before I ask the AHJ to consider
this change? 

Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to