We usually use the TYCO Riser Manifold which can be ordered with the relief
valve and install them in the riser room.  This is then piped as part of the
main drain.  The exit point is the only real consideration since water will
be dumped.  The location just needs to be relatively free of pedestrian
traffic, especially in freezing conditions. AGF also makes a T & D for the
same purpose.