Hi Tom,

The contractor called to tell us that the BFP manufacturer is aware and will
remedy. Apparently theres an issue with the 1st check.

Again thanks to all who responded. 

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross
Sent: Monday, April 30, 2007 4:54 PM
To: [email protected]
Subject: RE: Ames RPZ BFP

Maybe...
But I suspect he's got a problem with the cam checks.
Tom
GRS



John,

Our Technical Support receives calls on this topic regularly. I will not
point to a specific manufacturer, however some are worse than others. The
problem your are experiencing is trapped air in the sprinkler system. There
are two steps to correct this. The first in regards to adjusting the retard
delay, move the trip stem down manually and time the flow switch. This will
give you and idea of where the flow switch is working. The next step is to
drain the sprinkler system and have them fill if SLOW, painfully slow in
fact. While the system is filling, open every downstream drain, test
connection etc. This will help evacuate the air as the system is filling. if
there are any high points bleed the air at those points or install and
automatic air release system.

The phenomena that you are witnessing is an air pocket in the system
contracting and relaxing. The check valves are opening as the air pocket
constricts and the y close as the air pocket relaxes. The pressures are
equalizing and to prevent "back flow" the RPZ is closing preventing water
from entering the system. Remember a flow switch is mechanical device and
that vane is reacting to waterflow from 4-10 gpm. If the system is flowing
less than 4 gpm or stopped, the flow switch will reset.

Kind Regards,
Tm Frankenberg

>>> "John Drucker" <[EMAIL PROTECTED]> 4/30/2007 3:24 PM >>>

During waterflow alarm testing on a Wet Pipe NFPA-13 System I witnessed
a phenomena wherein the vane type waterflow switch fluctuated back in
forth appx every 10 seconds making it impossible to set a 30 second
retard. Supply Pressure is 60 psi static, 55 psi Residual at 2" Main
Drain Test.  The WF Switch is mounted horizontally in a straight length
of  6" Sch 10  48" from closest change in direction. Inspectors test is
located downstream end of a branch line 1/2" orifice in place.

The sprinkler contractor suspects theres a problem with this particular
BFP. Anyone had a similar problem.

Thanks

John Drucker


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to