Charles,

NFPA 13 (2002)  8.3.5 Thread Size Limitations

Tony Liddic, CET
Fire Sprinkler Designer
AEC Fire & Security
400 Fame Rd.
West Carrollton, OH  45449
937-866-4158
937-865-0212 fax
[EMAIL PROTECTED]

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Charles
Thurston
Sent: Friday, May 04, 2007 2:12 PM
To: Greg McGahan
Subject: Re: 1/2" thread - 8 K sprinklers

Hello Greg,



Wednesday, April 25, 2007, 12:19:42 PM, you wrote:

> NFPA 13 clearly states that we can not use 8.0 k heads with 1/2" threads
in
> new installations. I assume there are reasons for this but I do not know
> them.

Does anybody have the chapter and verse where it states this handy ? I
can not find it.



> BUT, we have a new job with pipe on the floor and 1/2" welded outlets for
> 5.6 k sprinklers. The problem is we ran into some lights and are having to
> move some pipe which blows our calcs. (Our designer made a mistake and did
> not realize that the lights are not hanging, but are mounted to the
> purlins.)

> We had in excess of 10% cushion and now we have -5%. If we use the 8K
heads
> we are fine. 

> The other option is to reorder all of the branchline piping 1 size larger.

> We reflowed the hydrants to confirm the water and lost 10 psi residual to
> make matters worse.

> Does anyone on the committee have any input before I ask the AHJ to
consider
> this change? 

> Greg

> Living Water Fire Protection, LLC
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> Fax: 850-937-1852



> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)


-- 
Best regards,
 Charles                            mailto:[EMAIL PROTECTED]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.467 / Virus Database: 269.6.2/787 - Release Date: 5/3/2007 2:11
PM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.467 / Virus Database: 269.6.2/787 - Release Date: 5/3/2007 2:11
PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to