This one is stumping the engineer, arch, AHJ and now me.

We have a Hilton high rise motel with soffits around the perimeter of the
rooms with res pendent sprinklers on opposing sides. The owner has
instructed the GC to install 1X8 and some 1x10 boards vertically from wall
to wall under the soffits on the walls adjacent to exterior walls with
windows as a valence. The sprinklers will all be obstructed according to the
book as they are only inches away from the valence.

The AHJ has suggested that if the valences are 8" deep and 8" off the
exterior wall the soffit rule may apply. I disagree in principle because
they are not soffits and will not behave like soffits in the event of a fire
(thanks to Roland's input on past issues).

The valences were not on the drawings and the building is slated to open in
2 weeks.

The question is that if the owner had waited until he got the CO and done
this, or if he had used normal valences would this be an issue? Is this more
of a decorative item that we can not predict or control, or is this really
an obstruction?

What do we do with this one? I am hoping that some of you with sprinkler
testing experience can help with this one.