Thought so, but needed to check.

At 12:05 PM 5/23/2007, you wrote:
THere  is nothing about excluding the tub because you now have to
INCLUDE that area

Roland

On May 23, 2007, at 5:44 AM, Todd Williams - work wrote:

There was some scuttlebutt a while back about not including the
area of the tub/shower when calculating the area of a bathroom
(within dwelling unit) to determine if sprinklers are required.
There is nothing in NFPA 13 2002 to support this. Should we include
the tub within the area calc? I usually include it as a mater of
course, but am working on a project where this could be the
difference between yes and no.

BTW, is the Forum working or have I been banned?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to