(1) the presence of the gypsum board does not change the construction to
non-combustible.

(2) good question, that one is not clear to me.  My initial response
would be "yes", but the requirement is vague.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Shawn
Fenneran
Sent: Wednesday, May 23, 2007 2:42 PM
To: [email protected]; Bob Caputo
Subject: Combustible Construction Stair Ways

To all:
I am doing a Project 4 Story Residential building witch is designed per
NFPA
13 and it is being built with Type V Construction. The Stairs are being
sheet rock w/ 1 layer of 5/8" GWB underneath all landings, and all walls
in
the stair. It does state in NFPA 13 8.14.3, Combustible Construction.
Sprinklers shall be installed beneath all stairway of combustible
construction.
(1) Does putting 5/8" GYB Sheet rock underneath the landing makes this a
Non
combustible stair?
(2) If this is considered a combustible stair do we have to put
sprinklers
underneath all landings, not just underneath the entry on each floor,
including underneath the intermediate landing between the floors

Thanks
Shawn Fenneran
CET#105218



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to