If you bias your sprinkler location (9 ft
rule) on your landings-with-doors, such that
it is towards the steps leading down,
ensuring the sprinkler spray down to the
landing below is not grossly
obstructed by the stairs leading-up,
you should get sufficient water on the
intermediate landing from this sprinkler
half-a-flight up.

   intermediate landing:  4 ft wide
   lateral distance of treads:  7.5 ft wide


This would protect the wood
treads and risers and landing.  Nothing
else SHOULD be in the stairways, and
rarely is at intermediate landings. Light
hazard is more than sufficient water.

In the past, I have gone with sprinklers on
landings with door access/egress--and
left intermediate landings bare, except
for firefighters hose connections in cases
where connections were required.

If the risers and treads are combustible,
and storage could happen underneath
the bottom flight of stairs, I would put
a sprinkler under there, as well.


Scot Deal
Excelsior Fire




 >(1) Does putting 5/8" GYB Sheet rock underneath the landing makes this a
Non
>combustible stair?
>(2) If this is considered a combustible stair do we have to put
sprinklers
>underneath all landings, not just underneath the entry on each floor,
>including underneath the intermediate landing between the floors