I think there is a seminar tomorrow at the NFPA
conference in Boston that may touch on this. If you start peddling now......
At 04:32 PM 6/4/2007, you wrote:
Thank you for such a good question and answer.
Are there any comments or studies about the
influence of cold air [air conditioning ]
blowing air at the sprinkler? Would the cold air
delay the response of the sprinkler?
mario berrios
[EMAIL PROTECTED]
-----Original Message-----
From: [EMAIL PROTECTED]
To: [email protected]
Sent: Tue, 8 May 2007 3:10 pm
Subject: RE: Sprinklers located next to diffusers
Typical ceiling diffuser is blowing air downward, (actually in an
mbrella type pattern, but who's to argue) A sidewall or side of duct
ounted type would be considered horizontal.
By the definition and the directions in the table it looks like you need
o be at least 1'-0" from the edge of the diffuser so if you're 1'-1"
ou should be good to go with an Ordinary Temp. You're mighty close
hough.
raig L. Prahl, CET
ire Protection Group
echanical Department
H2MHILL
ockwood Greene
500 International Drive
O Box 491, Spartanburg, SC 29304-0491
irect - 864.599.4102
ax - 864.599.8439
[EMAIL PROTECTED]
ttp://www.lg.com
----Original Message-----
rom: [EMAIL PROTECTED]
mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
ent: Tuesday, May 08, 2007 2:45 PM
o: [email protected]
ubject: Sprinklers located next to diffusers
Looking at Table 8.3.2.5a in 13-2002 there is a downward and horizontal
iffuser. For the standard 2x2 diffuser in a suspended ceiling which is
he correct to use. It is blowing air downward and horizontal? Can I
nstall an ordinary temp pendant sprinkler 1'-1" away from one of these
iffusers?
Thanks
______________________________________________
prinklerforum mailing list
[EMAIL PROTECTED]
ttp://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
o:[EMAIL PROTECTED]
Put the word unsubscribe in the subject field)
______________________________________________
prinklerforum mailing list
[EMAIL PROTECTED]
ttp://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
Put the word unsubscribe in the subject field)
________________________________________________________________________
AOL now offers free email to everyone. Find out
more about what's free from AOL at AOL.com.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)