Actually, right now I'm designing a very similar store and in the specs and
details it says the same thing in reference to all piping. We have installed
many and they have never enforced the branch line piping. However I have
noticed in some stores Like Wally world the branchlines are run at those
locations and where the head spacing did not work out they had short
armovers for those particular uprights. Bad thing is I'm having a time just
getting bottom chord sizing for bar joist and girders, I can only imagine
trying to get webbing layouts. I'm interested to know how it turns out. Good
luck.

Bobby Gillett
Designer
[EMAIL PROTECTED]
(731)-424-0130
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matthew Stone
Sent: Wednesday, June 13, 2007 12:08 PM
To: [email protected]
Subject: Hanging branch lines from panel points

We are installing a grid system in a super store and the general contractor
is demanding that we hang all piping within 6" of a panel point of the
web-type roof joist.  There is a detail showing sprinkler pipe to be
installed in this location and a structural drawing showing the location of
the main.  We naturally installed the main to meet these criteria.  The
branch lines are run perpendicular to the joists so hangers for the branch
lines are spaced at 6'-0" apart which is at every joist.  This means that
there is a 23 lb load at each hanger.  Table 9.1.1.6.1(b) requires a 2 × 2 ×
1/8 angle iron and the joists have a 2 x 2 x 3/16 angle iron on top. 
   
  Has anyone else come across this requirement in the contract drawings and
had it applied to all sprinkler pipe?
   
  We can use trapeze hangers to meet this demand by the GC but it will also
raise the question in those of you who look up when you are in super stores,
"Was this system installed by a licensed contractor?”
   
  Matthew Stone
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]