NFPA 13 states the following.

8.15.1.2.10  Concealed spaces where rigid materials are used and the
exposed surfaces have a flame spread index of 25 or less, and the
materials have been demonstrated not to propagate fire when tested in
accordance with NFPA 255, Standard Method of Test of Surface Burning
Characteristics of Building Materials, extended for an additional 20
minutes in the form in which they are installed, shall not require
sprinkler protection.

I have a foam insulation sprayed on the walls of an otherwise
non-combustible concealed space, that has a 25 or less flame spread that
is marketed as flame retardant in accordance with ASTM E84 (same as the
NFPA 255 test). 

Can anyone educate me on what  "and the materials have been demonstrated
not to propagate fire when tested in accordance with NFPA 255, Standard
Method of Test of Surface Burning Characteristics of Building Materials,
extended for an additional 20 minutes in the form in which they are
installed" means?  

Considering that the tunnel test measures materials installed on the
tunnel ceiling so I am not sure what this code language means.  Can
anyone shed some light/committee members?

Would you accept the material in a non-combustible concealed space?

Thanks