Well,
A contactor head bang the sprinkler head,
The sprinkler initiated and it was enough to use a bucket to contain what
came out of it. 

We then dismantled 116 heads and so on. 

The galvanized pipes were found clean. 

Regarding " I've not heard of this" 

It is not a normal practice to dismantle sprinklers for periodic inspection.


I've not head about it before, myself. 

Dan Arbel
Tel: 972-4-8243337
Fax: 972-4-8243278
M: 972-52-2810593

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Scott A.
Futrell
Sent: Thursday, June 28, 2007 1:13 PM
To: [email protected]
Subject: RE: Sprinkler Success Story

What led you to suspect there was "a great deal of clogged heads" on a
four year old system?

 

No, I've not heard of this.

 

Scott Futrell

 

(763) 425-1001 Office

(612) 759-5556 Cell

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Thursday, June 28, 2007 4:01 AM
To: [email protected]
Subject: RE: Sprinkler Success Story

 

Dear Forum members,

 

I have got the following situation.

 

A 4 years old system, grid type, 2" galvanized pipes, K=5.6 pendent

sprinklers, bulb type. 

 

Suspecting that there is a great deal of clogged heads, we run some
tests:

 

1.          We subjected a sample to 15 psi pressure and initiated the
bulbs. 

2.         Some of the heads burst.  Some did not. 

3.         One head burst at 14 bars, one at 3.5 bars, one at 1.5 bars. 

4.         In the sprinklers that bust, the cone type plastic plug was
ejected,

but the deposit did not, i.e.:  The actual nozzle was about 1/4 of the
full

sprinkler bore area. 

 

We tested the water. 

 

The general solid contents were between 277 and 455 mg/L.  

 

Ca was between 55 and 82 mg/L, 

 

Mg 32 to 37 mg/L. 

 

Cl  25 to 27 mg/L

 

Na 14 to 17 mg/L

 

Zn 3 to 6 mg/L

 

We also tested the deposits within some sprinklers that appeared to be
hard

(resulting in a constricted nozzle). 

 

In these deposits we found a great deal of Iron and Zinc.  

 

In the deposit one head we found 4% Ca, 50% iron and  4.4% Zinc,

 

In another one 10% Ca, 1.5% Iron and 20% Zinc. 

 

Another one 4.5% Ca, 25% Iron, 8% Zinc. 

 

All came from the same galvanized system. 

 

This is all very disturbing information. 

 

It appears that Zinc and Iron ions migrate to the copper based sprinkler
and

creates hard deposit de-capacitating the sprinkler system. 

 

I would like to hear from other people experience and source of
information

for similar research. 

 

After all, under NFPA25 one is not supposed to inspect the condition of

sprinklers by dismounting a sample. 

 

DAN, 

 

Dan Arbel

Tel: 972-4-8243337

Fax: 972-4-8243278

M: 972-52-2810593

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 

To Unsubscribe, send an email
to:[EMAIL PROTECTED]

(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


__________ NOD32 2361 (20070628) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to