I know of a lot of quality issues with galvanized pipe that is coming
out of China.  Does this happen to be Chinese pipe?

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Thursday, June 28, 2007 10:44 AM
To: [email protected]
Subject: RE: Sprinkler Success Story

This is a standard wet type system. 

Dan Arbel
Tel: 972-4-8243337
Fax: 972-4-8243278
M: 972-52-2810593

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Thursday, June 28, 2007 2:47 PM
To: [email protected]
Subject: RE: Sprinkler Success Story

Dan,

Is this a dry pipe or pre-action system?
Did the pipe happen to be made in China?
Was there any testing for the presence of the microbes associated with
MIC?
What type of sprinklers were these?

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Thursday, June 28, 2007 5:01 AM
To: [email protected]
Subject: RE: Sprinkler Success Story

Dear Forum members,

I have got the following situation.

A 4 years old system, grid type, 2" galvanized pipes, K=5.6 pendent
sprinklers, bulb type. 

Suspecting that there is a great deal of clogged heads, we run some
tests:

1.      We subjected a sample to 15 psi pressure and initiated the
bulbs. 
2.      Some of the heads burst.  Some did not. 
3.      One head burst at 14 bars, one at 3.5 bars, one at 1.5 bars. 
4.      In the sprinklers that bust, the cone type plastic plug was
ejected,
but the deposit did not, i.e.:  The actual nozzle was about 1/4 of the
full
sprinkler bore area. 

We tested the water. 

The general solid contents were between 277 and 455 mg/L.  

Ca was between 55 and 82 mg/L, 

Mg 32 to 37 mg/L. 

Cl  25 to 27 mg/L

Na 14 to 17 mg/L

Zn 3 to 6 mg/L

We also tested the deposits within some sprinklers that appeared to be
hard
(resulting in a constricted nozzle). 

In these deposits we found a great deal of Iron and Zinc.  

In the deposit one head we found 4% Ca, 50% iron and  4.4% Zinc,

In another one 10% Ca, 1.5% Iron and 20% Zinc. 

Another one 4.5% Ca, 25% Iron, 8% Zinc. 

All came from the same galvanized system. 

This is all very disturbing information. 

It appears that Zinc and Iron ions migrate to the copper based sprinkler
and
creates hard deposit de-capacitating the sprinkler system. 

I would like to hear from other people experience and source of
information
for similar research. 

After all, under NFPA25 one is not supposed to inspect the condition of
sprinklers by dismounting a sample. 
 
DAN, 

Dan Arbel
Tel: 972-4-8243337
Fax: 972-4-8243278
M: 972-52-2810593

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


__________ NOD32 2361 (20070628) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to