If it is a drain line, you would include it in the hydraulic calculations WHY??


Jeff Hewitt, PE, SET, SFPE (Prof. Member)
Corporate Engineer
Bi-State Fire Protection Corporation
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one or more legal privileges. It is intended solely for the use of the addressee identified above. If you are not the intended recipient, any use, disclosure, copying or distribution of this e-mail is unauthorized. If you received this e-mail in error, please notify the sender immediately at the above captioned address.

----- Original Message ----- From: <[EMAIL PROTECTED]>
To: <[email protected]>
Cc: <[email protected]>; <[EMAIL PROTECTED]>
Sent: Thursday, June 28, 2007 9:39 AM
Subject: RE: Gang Drain for Attic Dry System


Even though the 1 inch pipe does not seem to increase the gridding effect,
it still must be provided in the hydraulic calculations where it can end up
show some surprising effects.

Thank You

Rahe Loftin, P.E.
Region 7 - GSA
Office - 817-978-7299
Fax - 817-978-8644
Cell - 817-371-3102





            "Matthew J.
            Willis"                                                    To
            <[EMAIL PROTECTED]         [email protected]
            fp.com>                                                    cc
            Sent by:
            sprinklerforum-bo                                     Subject
            [EMAIL PROTECTED]         RE: Gang Drain for Attic Dry System
            er.org


            06/28/2007 09:32
            AM


            Please respond to
            [EMAIL PROTECTED]
             resprinkler.org






Yes... But see 8.15.2.5.3.4 (02). The handbook gives a good commentary if
available. The piping is limited to 1", so you do not increase the gridding
effect.

R/

Matt

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]


----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On
----- >Behalf Of [EMAIL PROTECTED]
----- >Sent: Thursday, June 28, 2007 9:24 AM
----- >To: [email protected]
----- >Subject: Gang Drain for Attic Dry System
----- >
----- >
----- >This question was just posed to me by my Branch Manager -
----- >
----- >In an attic dry system with each branch line ending in
----- >what amounts to a "low?point", if the designer
----- >interconnected each branch line to?a 1-inch gang drain,
----- >would that not, in effect, create a gridded dry system?
----- >
----- >Ray Hoshall
----- >Service Manager
----- >FIRE TECH SERVICES, INC.
----- >
----- >_________________________________________________________
----- >_______________
----- >AOL now offers free email to everyone.  Find out more
----- >about what's free from AOL at AOL.com.
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to