Travis, If I'm reading 8.14.4.4 (2002 ed) correctly, you do not need the closely spaced sprinklers if our adjacent floor areas are all fully sprinklered, the horizontal openings are at least 20', and your atrium area is greater than 1000 sf. From your posting, it sounds as if you meet all three determining factors.
Bob Knight -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack Sent: Monday, June 25, 2007 5:20 PM To: [email protected] Subject: RE:Atrium Would an open atrium of 1400 sq ft in a 3 story building require closely spaced sprinklers around it? The atrium is located in the middle of an open office area. There is no glass or anything around the atrium. There is a handrail around the perimeter of the atrium on the upper levels? I am getting conflicting information on if the closely spaced sprinklers are needed or not? Travis No virus found in this outgoing message. Checked by AVG Free Edition. Version: 7.5.472 / Virus Database: 269.9.1/854 - Release Date: 6/19/2007 1:12 PM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)