Travis,
If I'm reading 8.14.4.4 (2002 ed) correctly, you do not need the closely
spaced sprinklers if our adjacent floor areas are all fully sprinklered, the
horizontal openings are at least 20', and your atrium area is greater than
1000 sf.  From your posting, it sounds as if you meet all three determining
factors.

Bob Knight



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack
Sent: Monday, June 25, 2007 5:20 PM
To: [email protected]
Subject: RE:Atrium

Would an open atrium of 1400 sq ft in a 3 story building require closely
spaced sprinklers around it?  The atrium is located in the middle of an open
office area.  There is no glass or anything around the atrium.  There is a
handrail around the perimeter of the atrium on the upper levels?  I am
getting conflicting information on if the closely spaced sprinklers are
needed or not?

Travis