I believe part of the answer lies in whether or not this space is a true
atrium.  If it meets the definition of an atrium then the fuel loading
on the floor of the space is limited to low hazard uses and only
approved materials and decorations.  There is an exception within the
code, that indicates that since the atrium space is being provided with
sprinklers, the atrium floor area is permitted to be used for any
approved use.  The key words are approved use which is where the AHJ has
the say so.  In my experience the AHJ has typically followed the low
hazard rule even when providing sprinklers.  The second item is that if
it is an atrium, then a smoke control system is required.  This system
is required to be installed and evaluated per Section 909 of the IBC and
NFPA 92B.  Therefore, you would not want to drop the buoyant smoke as
the intent and design of the system is to lift the smoke above the
occupiable floor areas to create a tenanble environment.  

There are also protective measures that can be taken to separate the
atrium sprinklers from the sprinklers for the rest of the building.  IF
you would like to discuss these, please contact me off-line.  

Thanks,   
 
Carl Chappell
Phone: (702) 699-5391
Fax: (702) 699-5534
Cell: (702) 400-8736



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, December 27, 2007 10:27 AM
To: [email protected]
Subject: Re: Atrium

Sounds like someone is blowing smoke up your..... well lets not go  
there.  The point is that, you can't eliminate buoyant smoke.  You  
eliminate the buoyancy of the smoke so that it drops to the floor.  I  
haven't seen any hard data on what density is required but applying  
logic (which can lead one astray), once you are away from the fire  
plume and simply pulling the heat out of the smoke, a high density is  
not required.

It may be that their intent to  provide enough overkill so that they  
believe the fire will be knocked out avoiding the production of smoke  
but I'm just guessing.  Equivalencies for performance based BUILDING  
design should have a high level of clarity.  Is there more  
information that the AHJ/building official (ie stakeholders) have  
seen in accepting this approach?

Roland

On Dec 27, 2007, at 9:49 AM, Joe Burtell wrote:

> This atrium is for a cancer center/clinic. I don't have any furniture
> layouts but I am sure they will have some seating, information  
> desk, etc....
> This is also not a FM project. Any thoughts of the OH1 balconies for
> elimination of buoyant smoke?
>
> Joe Burtell, SET, CFPS
> Burtell Fire Protection, Inc.
> [EMAIL PROTECTED]
> www.burtellfire.com
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to