Hello Greg,
Since I am not doing any high rise work "yet" I have not been
involved in the pool connection issue. I do know most of the new high
rise buildings built here in the last couple of years have a line from
the pool to the Fire Dept access point so the pumper can connect and
draw from the pool if needed. I am talking about Ocean Front properties
where the water table is 10-12 feet in places.
As a side note we do service a property where the pool is the
only water supply, Even has a vacuum pump tied into the supply side
line of the pump to prime the line. When it was built it was far enough
out there was not any city water supply and the pool is filled from
the well.
Friday, July 6, 2007, 1:39:24 PM, you wrote:
> 2 other potential problems...
> We were involved in a job where the Insurance Carrier forced the building
> owner to remove the pump suction line from the pool and install a new water
> source for liability concerns.
> During this project on the Gulf of Mexico, the engineers were concerned that
> the pool would float out of the ground if left empty too long. Supposedly
> has happened before.
> Greg
> Living Water Fire Protection, LLC
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> Fax: 850-937-1852
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill
> Sent: Friday, July 06, 2007 12:30 PM
> To: [email protected]
> Subject: RE: pool as water source
> The disembowelment was here in MN. The news has reported the cover plate
> was missing from the suction in the pool. Granted the news reported this
> and we know how they mess up sprinklers....
> Vortex plates, large inlets and multiple draft points should lessen the
> risks.
> In a very low water supply area in town we used a pool at a college campus
> for a back up supply. The systems ran off the grid and pump but it was so
> tight the pool was added as reserve. It's been about 8 years. The only
> point that sees chlorine is a short run on the suction side of the pump to
> the check valve in the city line. The system is filled with potable water
> (or what used to be potable before it sat around in sprinkler piping.) The
> only time the system will have pool water is if the city grid doesn't keep
> up with the demand because either the grid is light at the time of fire, the
> FF use any water or the system opens more heads than code designed.
> If you can fill and do T&M with potable water you can limit the chlorine
> damage to just when fires occur. Allow a means do drain and flush after a
> fire (or inadvertent fill with chlorine). Then a little chlorine is a small
> part of the problem.
> Great idea, probably not. Manageable when necessary, yeah.
> Chris Cahill, P.E.
> Fire Protection Engineer
> Sentry Fire Protection, Inc.
>
> 763-658-4483
> 763-658-4921 fax
>
> Email: [EMAIL PROTECTED]
>
> Mail: P.O. Box 69
> Waverly, MN 55390
>
> Location: 4439 Hwy 12 SW
> Waverly, MN 55390
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
> Sent: Friday, July 06, 2007 12:11 PM
> To: [email protected]
> Subject: RE: pool as water source
> Steve:
> That's a horrible story - made me squirm.
> Do you have any specific information regarding the issue of water
> chemistry and advancing corrosion? Coincidentally, I have a prospective
> project here in SoCal where the developer wants to consider using the
> pool for a high-rise water supply. I think that the suction vortex
> could be mitigated with a Weir-type box taken off to the side of the
> pool, but I'm ig'nant when it comes to chlorine and piping.
> Steve Leyton
> PROTECTION DESIGN & CONSULTING
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Steve
> Kowkabany
> Sent: Friday, July 06, 2007 9:57 AM
> To: [email protected]
> Subject: RE: pool as water source
> Rod,
> There are a few things to be cautious of. We considered using pools for
> several projects and opted not to for a few reasons including the
> following:
> 1) Safety - A fire pump will pull a pretty strong draft on a swimming
> pool.
> There is a story on CNN.com right now about a 6 year old girl who was
> disembowled after being on top of the drain of an emptying kiddie-pool.
> That was without any mechanically induced suction. On top of the risk
> of a
> horrific injury like that, there is the obvious threat of drowning
> someone.
> 2) Structural damage from buoyant forces on the pool from emptying it
> quickly - this probably isn't a problem for you, but for outdoor pools
> in
> areas with a high water table, it can happen.
> 3) Corrosion issues - chlorinated pool water is pretty nasty to metal
> pipe.
> Just a few things to keep in mind. Good luck,
> Steve Kowkabany, P.E.
> Fire Protection Engineer
> Neptune Fire Protection Engineering LLC
> 216 Seagate Avenue Unit B
> Neptune Beach, FL 32266
> 904-652-4200 Phone
> 904-212-0868 Fax
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Rod
> DiBona
> Sent: Friday, July 06, 2007 12:28 PM
> To: [email protected]
> Subject: pool as water source
> I am wondering what if there is anything I should know about using an
> indoor swimming pool as the water supply for a fire pump in a new motel.
> This is not a high rise building and this is the only source. I think
> this is somewhat common but we have never done this. Anything to be
> aware of? Thanks for your replies.
>
> Rod DiBona
> V.P. of Sales
> Rapid Fire Protection
> [EMAIL PROTECTED]
> 605-348-2342 ph
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
--
Best regards,
Charles mailto:[EMAIL PROTECTED]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)