I'm not familiar with the specifics of military work but let me offer some
insight from the non military code.

This situation may actually involve three codes.  First the National
Electrical Code which has authority with regards to wiring methods and
materials. The NEC identifies three different "air handling" arrangements.
1) "Ducts" 2) "Plenums" and 3) "Other Environmental Air Spaces".  The first
two Ducts and Plenums generally requires a metallic covering or enclosure of
the conductors, there are exceptions for plenum rated cable where entry into
the duct or plenum is required to serve a piece of equipment in the
airstream. The latter, "Other Environmental Air Spaces" includes the space
above a suspended ceiling used for return air. Quite often this is labelled
a "plenum" however within the context of the NEC this is incorrect.  The NEC
specifically permits certain types of speciality cables to be exposed in
this area and allows cables to be run through this area unlike ducts or
plenums.  Red FPLP fire alarm, or blue and yellow CMP communications and
data cable are examples.

The Mechanical Code however only contains two definitions with regards to
air handling and they are 1) "Ducts" and "Plenums".  With the context of the
mechanical code the space above a suspended ceiling is a plenum. Items that
are not regulated by the electrical code fall within the jurisdiction of the
mechanical code.  Here we will find that materials that do not fall with the
Flame Spread (25) and Smoke Index (50) requirements for these spaces are
prohibited.  PVC piping is an example of a prohibited material within a
plenum.

The Building Code also provides requirements with regards to combustibles in
concealed spaces, fire and draft stopping, etc. The use of a CPVC piping
system listed and tested in compliance with the E-84 standard is acceptable
pursuant to 2000 IMC 602.2.1. Of course there may be restrictions on its use
exposed unless the piping system is protected in accordance with its
listing.

In this example the sprinklers are resolving an electrical code violation,
non rated cable in a plenum. 

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey


 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Kowkabany
Sent: Thursday, July 12, 2007 12:08 PM
To: [email protected]
Subject: Non Plenum-Rated Cable in Non-Combustible Ceiling

I have an odd situation on a military job I am doing right now where we are
adding sprinkler protection to 100,000 sqft of office space in a 3-story
building that has been built in three phases over the past 25 years of
non-combustible construction.  We are planning on using CPVC piping for this
application to hopefully make the retrofit less labor intensive.  That's all
pretty straightforward but the problem arises from the fact that the base
communication department has been steadily adding  lots of non-plenum rated
cable on top of the drop ceiling into a non-combustible return plenum
ceiling space above the first and second floors.  The space above the
ceiling varies in depth from 4-5 feet with 16" deep fire proofed steel
joists spaced 3'-9" OC in some areas and 7'-6" OC in other parts.  As a
result, the military has recognized the life safety risk of this and allows
two options per the latest UFC-3-600-1, which are to either replace all of
the illegal cable over 5 years (impossible for us) or sprinkler above the
ceiling.  So we are adding sprinklers above the ceiling.  I'm a little
confused on a couple of things, and hope to get some guidance from anyone
who has run into similar situations:

 

1)      Can you typically still assume the ceiling space is non-combustible
and use CPVC piping if there is some non-plenum rated cabling in there?

2)      What is the best approach for sprinklering a ceiling space this deep
- standard K5.6 brass uprights spaced at a normal light hazard 225
sqft/head?  

 

Thank you very much in advance for any thoughts on this,

 

Steve Kowkabany, P.E.

Fire Protection Engineer

Neptune Fire Protection Engineering LLC

216 Seagate Avenue Unit B

Neptune Beach, FL 32266

904-652-4200 Phone

904-212-0868 Fax 

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to