IDOD is currently changing their production to allow pipe sizes up to 4
in. diameter. (previously limited to 2 in.)  It may not be immediately
available - not until the plant gets up and running again later in the
summer or early fall.  Check with your supplier or call IDOD directly.

It currently comes in Schedule 5 and Schedule 7 thicknesses. Both are
UL/FM I believe.

We've spec'd it before and like the final installed product.  No
problems from either of the contractors that did the installs.

Mark A. Sornsin, PE 
Fire Protection Engineer 
Ulteig Engineers, Inc. 
Fargo, ND  
701.280.8591
[EMAIL PROTECTED] 
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ken
Holsopple
Sent: Thursday, July 12, 2007 4:29 PM
To: [email protected]
Subject: RE: IDOD Dry pipe systems


OK it was sched 7 not sched 10. I was wong.

Best Regards,
Ken Holsopple
Design Manager 
Rowe Sprinkler Systems, Inc.
570-837-7647