Bill,

Perhaps. I see a lot of hose thread adapters installed on wet pipe main
drains. And there may be a legitimate purpose where the main drain
piping is below grade and this serves as a low point drain, i.e. attach
a hose to a floor drain to get the remaining water out. I also know that
"people" use this as convenient way to take water, albeit improperly.
Frankly I wouldn't drink out of this but the guy using this connection
for whatever might decide to take a "sip" from the hose. Again keep in
mind this would only apply where the fire protection water is from a non
potable source pursuant to  2006 NSPC 10.2. "In buildings where dual
water distribution systems are installed".  My opinion on this is where
the sprinkler system supply is taken from a non potable source such as a
pond, tank, cistern, etc.  In a building connected to a potable city
water source the referenced code section would not apply.

Has everyone taken a close look at 2006 NSPC 10.5.9 ?  However keep in
mind that there are two significant requirements of 10.5.9 in the 2006
NSPC.

2006 NSPC 10.5.9 - Exception (3) "Where fire protection include a fire
department connection, double check valve assemblies shall not be
permitted."  

2006 NSPC 10.5.9 - Exception (4) "Where fire protection are filled with
solution that are considered to be health hazards as defined in Section
1.2, double check valve assemblies shall not be permitted."

Backflow prevention and public health are apparently significant
concerns, anyone who's built a home know the plumbing inspector checks
for backflows on hose bibs.  As to the IPC I don't know.

John


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brooks,
Bill
Sent: Friday, July 13, 2007 9:31 AM
To: '[email protected]'
Subject: RE: Backflow: Sprinkler System Identification

John, what a reference!  This means we should be adding these signs to
our sprinkler system specifications.  Would you say one of these signs
should be provided at the termination of the inspector's test, at each
drum drip on a dry system, and at various low point drains on our
systems, etc, etc?  This is a serious question - do you think this is
the intent of 2006 NSPC 10.2?
Is this same provision in the International Plumbing Code?

Bill Brooks
Pittsburgh, PA

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of John
Drucker
Sent: Friday, July 13, 2007 9:16 AM
To: [email protected]
Subject: RE: Backflow: Sprinkler System Indentification



2006 NSPC 10.2 Identification of Potable and Non Potable Water "In
buildings where dual water distribution systems are installed, one
potable and the other non-potable water, each system shall be identified
by color marking or metal tags, or other appropriate methods such as may
be approved by the authority having jurisdiction. Each outlet on the
non-potable water line that may be used for drinking or domestic
purposes shall be posted: DANGER-UNSAFE WATER."

"Service and Background Color - Fire Protection = Red"

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to