Space w/ slope, use horizontal plane @ floor for remote area (22.4.4.6.8 2007). That was my thought, I agree. The other question: does that make each hip its own area for spacing as long as your sprinklers meet the min distance between sprinkler requirements(6'-0) across the hip and the "As" to the edge of the hip?
Bobby Gillett Project Manager [EMAIL PROTECTED] (731)-424-0130 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack Sent: Friday, July 27, 2007 9:22 AM To: [email protected] Subject: RE: Sprinkler layout under slope Space with the slope. Calculate using floor projection. That is how I was taught. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bobby Gillett Sent: Friday, July 27, 2007 7:18 AM To: [email protected] Subject: Sprinkler layout under slope Old rules~new debate here in the office. You have a 6:12 roof slope, 4 hips and very little ridge. Per 8.6.4.1.4 you place your highest and lowest sprinklers accordingly. The ones spaced along the slope as required are the ones in question. When spacing these parallel (up) to the slope, do you space them on a horizontal plane or with the slope. And do you space to each hip ( 4 individual spaces) or space across the hip ( one floor space) ? Bobby Gillett Project Manager [EMAIL PROTECTED] (731)-424-0130 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) __________ NOD32 2425 (20070727) Information __________ This message was checked by NOD32 antivirus system. http://www.eset.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)