Tony,

I'm probably wrong or misreading your question but I think the Tyco LF
II maximum would be based on their sprinkler performance under these
conditions whereas NFPA criterion is the minimum performance standard.
This bears out when you see NFPA has a minimum standard but no maximum
while Tyco LF II has both (beyond the standard) and QR merely meet the
standard. All are restricted to 8" maximum lintel depth but presumably
anybody that could prove there sprinkler performs per UL/FM at a 10'
(is their a tongue in cheek keyboard configuration similar to the I'm
making a joke :-) design?) lintel depth could have it listed thus.

On 8/13/07, A.P.Silva <[EMAIL PROTECTED]> wrote:
>
> NFPA 13, 2002; 8.7.4.1.3.1 states deflector to bottom of soffit to be
> MINIMUM 2 inches. The commentary in the handbook says depth of soffit is
> limited to 8 inches, to project water to the back wall. So wouldn't the
> deflector to bottom of soffit also affect spraying to the back wall, and
> thus be limited to MAXIMUM 2 inches? There is no comment in the handbook for
> the restriction of the deflector height above the bottom of the soffit.
>
> If not, is there a maximum?
>
> Tyco Series LFII, residential sprinkler design guide, figure 4, part 2,
> limits MAXIMUM distance to 4 inch. (Tried checking design guides in the web
> for Reliable, Viking and Victaulic for comparison but for some reason been
> unable to download them, maybe my server is currently too slow)
>
> The problem is residential heads (TYCO LFII) have been installed in an 8
> inch wide soffit (in a residential corridor), with the deflector 7 1/2"
> above the bottom of the soffit. It clearly violates the TYCO design
> guidelines. I'm looking at recommending replacing with standard q/r heads
> (provided the hydraulics work, of course). Is that an option?
>
> Going by the available info, it should be okay, as NFPA does not give a
> maximum value. However, I am worried whether it is an error in NFPA.
>
> Anyone out there has given this some thought?
>
> Tony
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to