I guess that was the point I was trying to make. Is the problem the size of the home or the very specific hazard we are trying to protect? We haven't done any homes that large, but we've done 15k s.f. houses with attached greenhouses, indoor swimming pools, and one with indoor basketball court (1/2 court only). I am less concerned about the actual size of the house - more concerned about the proper application of the system for the hazard.
Jim Kettler > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] Behalf Of Steve > Leyton > Sent: Monday, August 20, 2007 01:49 PM > To: [email protected] > Subject: RE: large single family houses > > > Jim: > > What if that "single room" is 4,000 s.f. with ceilings that > peak at 30' > and have pockets, beams, suspended obstructions, catwalks, > lofts, etc., > etc., etc.? I agree that some measure of additional protection is > appropriate for these mega-homes, as both the fire load and volume of > space in selected compartments can be WAY beyond what we see in > "typical" homes. > > Steve Leyton > Protection Design & Consulting > > >