The other day, I ran across an FMG Inspector at a Big Box Store.
He was testing fire pumps. To measure flow, he used 2 Pollard Hydrant  
Diffusers with built in Pitot Gauges and screwed them onto the Pump  test 
header.
He then walks back and forth as he opens the valve, checks readings,  etc.
 
Now, I found this interesting because we've always used 2 fitters to test  
pumps...and this guy just fly's around the country with these diffusers.
 
Way to save labor?
 
I called Pollard water, and the individual I spoke with said the hydrant  
Diffusers are listed for Fire Hydrant Flow Testing, and did not believe they  
were listed or approved for Fire Pump Flow Testing.
I also know the valves on the test header can sometimes "walk" when you are  
doing the test, and by the time you walked from the valve to the diffuser, the 
 valve may have moved a little.
 
Does anyone else test Fire Pumps in this manner? The FMG guy also did not  
use the NEC Face shield, gloves and rubber mat...which I have been told is  
required per OSHA and NEC.
 
I'd really like to know how the more experienced contractors are conducting  
these tests
 