OK, Tom. You've been pushing these pitotless nozzles. It looks like a
great toy, but what justifies the $495 dollar cost? (I know, this
should be on Sprinkler Chat, but it is a segue from a technical Q, so
I figured it was OK.)
At 06:07 PM 8/20/2007, you wrote:
I have tested many fire pumps all by my lonesome before, I prefer a helper
but in a pinch have done it alone. He should have been modulating with the
OS&Y or BV and not with those straight gates, they do walk and are not
supposed to be used for anything but full open or full closed, imho. So
he's also pressurizing the normally empty test header line and fittings too?
Big boo-boo. I'm not sure about UL having a category for "fire pump testing
devices" but I use Hosemonsters (you guys gotta get those pitot-less FM
approved nozzles, they're fantastic!) and/or digital flowmeters. My
hosemonsters have a remote reading assembly with 25', 50' and 100' tender
lines that allow me to read the pitot pressures away from the water at the
test header, on the gate of the truck or right in the Fire Pump Room.
So yes, a pump can be tested by one person. If the area is closed off and
no danger to pedestrians, easy for one sole. I rarely use 2 helpers unless
it's a real big one. I did a 2500 GPM at the local IKEA this morning with
just myself and my large baby brother, no problem. 6 lines and monsters,
remote reader and radios. Took 45 minutes and that included 3 auto and 3
manual starts and stops of both pumps, transfer switch test and emergency
starts on both normal and emergency. I easily could have done it myself
too.
I've got 7 more to do this week, a couple I'm doing myself. There are still
some shops in my area doing the old playpipe thing (I use them rarely)
whether under planks under the truck wheels or those playpipe trailers but
you gotta check out hosemonsters and with the new 2" nozzles, you can cut
out at least one line on most pump tests. I cringe when I see others just
blowing water down the drain for an hour, fooling with hose gates on
playpipes with the header and hose subject to full pump discharge pressure.
3 flow points take 20 minutes if you know what you are doing. BTW-I've got
2 of those hydrant testers, I doubt their accuracy.
Tom Duross
Go Red Sox!
The other day, I ran across an FMG Inspector at a Big Box Store.
He was testing fire pumps. To measure flow, he used 2 Pollard Hydrant
Diffusers with built in Pitot Gauges and screwed them onto the Pump test
header.
He then walks back and forth as he opens the valve, checks readings, etc.
Now, I found this interesting because we've always used 2 fitters to test
pumps...and this guy just fly's around the country with these diffusers.
Way to save labor?
I called Pollard water, and the individual I spoke with said the hydrant
Diffusers are listed for Fire Hydrant Flow Testing, and did not believe they
were listed or approved for Fire Pump Flow Testing.
I also know the valves on the test header can sometimes "walk" when you are
doing the test, and by the time you walked from the valve to the diffuser,
the
valve may have moved a little.
Does anyone else test Fire Pumps in this manner? The FMG guy also did not
use the NEC Face shield, gloves and rubber mat...which I have been told is
required per OSHA and NEC.
I'd really like to know how the more experienced contractors are conducting
these tests
Forest
Cherokee Fire
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]