As a corallary to this question, what about a building constructed of steel
beams / joists and metal roof deck that also has a 10' tall x 10' wide wood
truss framed mansard sitting atop the perimeter of the roof.  I realize it
is a combustible concealed space.  However, nothing is going to be in the
space.  There is no access from the roof below to the mansard.  It is for
architectural looks only.  If there was a leak in this space, you would not
know until there was significant amount of water.  Would this space need to
be protected?  If not, can you point to a section that would allow it to be
omitted?

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Wednesday, August 22, 2007 11:48 AM
To: AFSA
Subject: Parapets

What is the norm when dealing with parapets which are so constructed as to
create a small (8 sq. ft. x 20’ long) combustible concealed area within.
This parapet is separated from the interior of the attic by the plywood roof
decking. I’m trying to relate it to the requirements in nfpa13 2007, 8.15.7
because if areas beneath floors can be non-sprinklered then surely a parapet
would qualify as so not requiring sprinklers. Wouldn’t it?

 

Ron


Internal Virus Database is out-of-date.
Checked by AVG Free Edition. 
Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007
1:39 PM
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

__________ NOD32 2475 (20070822) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to