Neither did the room where 3 electrician died in, I think, Idaho a few years
back.
Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
763-658-4483
763-658-4921 fax
Email: [EMAIL PROTECTED]
Mail: P.O. Box 69
Waverly, MN 55390
Location: 4439 Hwy 12 SW
Waverly, MN 55390
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reza Esmaeili
Sent: Thursday, August 23, 2007 9:59 AM
To: [email protected]
Subject: Re: Carbon Dioxide System Discharge Time
Jim,
I forgot to explain, the room doesn't have any operators at all, and
carbon dioxide is the best choice.
Thanks,
Reza
[EMAIL PROTECTED] wrote:
Reza:
I would not recommend a CO2 system as it is potentially too dangerous. I
would consider a clean agent sytem per NFPA 2001.
Hopefully, this is only a back-up to a wet pipe system, which is still my
favorite.
Regards,
James L.(Jim) Roberts, PE, SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)
Reza Esmaeili
Sent by: To
[EMAIL PROTECTED] [email protected]
prinkler.org cc
08/23/2007 10:18 AM
Please respond to Subject
sprinklerforum Carbon Dioxide System Discharge Time
Hi all,
For designing a total flooding high pressure carbon dioxide system in a
3,500 cubic feet computer room with electrical equipment and cable runs, I
have specified my room as "Dry electrical hazard" with flooding factor of
0.083 lb/cubic.feet and 50% design concentration according to NFPA-12.
My questions are as below:
1)- Is a computer room fire a deep seated fire?
2)- NFPA 12 states that "For deep-seated fires, the design concentration
shall be achieved within 7 minutes, but the rate shall be not less than
that required to develop a concentration of 30 percent in 2 minutes." Is it
a problem if the total discharge time would be only 1 minute for this case?
Many thanks for your help in advance.
Reza
---------------------------------
Pinpoint customers who are looking for what you sell.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
------------------------------------------------------------
The information transmitted is intended only for the person
or entity to which it is addressed and may contain
proprietary, business-confidential and/or privileged material.
If you are not the intended recipient of this message you are
hereby notified that any use, review, retransmission, dissemination,
distribution, reproduction or any action taken in reliance upon
this message is prohibited. If you received this in error, please
contact the sender and delete the material from any computer.
Any views expressed in this message are those of the individual
sender and may not necessarily reflect the views of the company.
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
---------------------------------
Looking for a deal? Find great prices on flights and hotels with Yahoo!
FareChase.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum