Thanks All,
  Ford, if the intent of slow flow rate for deep seated fires is preventing 
over pressurization, so why NFPA-12 suggest high flow rate for Surface fires 
involving flammable liquids, gases, and solids? 
  NFpa12 States that "Surface fires are the most common hazard particularly 
adaptable to extinguishment by total flooding systems. They are subject to 
prompt extinguishment when carbon dioxide is quickly introduced into the 
enclosure in sufficient quantity to overcome leakage and provide an 
extinguishing concentration for the particular materials involved."
   
  NFpa12 also States that "For deep-seated fires, the required extinguishing 
concentration shall be maintained for a sufficient period of time to allow the 
smoldering to be extinguished and the material to cool to a point at which 
reignition will not occur when the inert atmosphere is dissipated."
   
  I think I explained at first in a bad manner. There are two protected area.
  1- Computer room: would be protected with FM-200 system
  2- Computer room subfloor with electrical equipment and cable runs: would be 
protected with high pressure carbon dioxide system.
  My question is about subfloor, while NFPA 12 states that "For deep-seated 
fires, the design concentration shall be achieved within 7 minutes, but the 
rate shall be not less than that required to develop a concentration of 30 
percent in 2 minutes." Is it a problem if the total discharge time would be 
only 1 minute for this case? 
  Thanks,
  Reza
   
  [EMAIL PROTECTED] wrote:
  I don't disagree just haven't had any of the sparky/computer types have
any warm fuzzies when you speak of wet pipe sprinklers. Usually with
reluctance they will accept the pre-action scheme but would rather have
nothing with water in the room at all. Then you explain the fact that
if there's a fire, the responders will most likely be bringing hoses in
and that sometimes gets their attention. 

In any case these types of situation are always a point of contention
mostly due to a lot of misinformation and fables.

But can you blame them with all those leaking, false tripping, deluge
systems they see on TV? 


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, August 23, 2007 11:29 AM
To: [email protected]
Subject: RE: Carbon Dioxide System Discharge Time

Craig:

I wasn't saying a pre-action sprinkler system instead of a wet pipe
system.
My preference is a wet system with independent smoke sensors tied to the
fire alarm system. The only time I use pre-action is when the owner is
the nervous type.

Otherwise, the water damage can be greater due to potential operation of
more heads due to the operational delay.

Regards,

James L.(Jim) Roberts, PE, SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)







Sent by:

[EMAIL PROTECTED]
To 
prinkler.org


08/23/2007 11:07 AM
cc 
Please respond to

sprinklerforum
Subject 
RE: Carbon
Dioxide System Discharge Time 


















Can the room be occupied at any time either by service personnel or
other occasional operators? Typically the answer would be yes as all
equipment needs human intervention at some time.

What Jim is saying is that a Pre-action sprinkler system would actually
be the best choice and the most cost effective with something like
FM-200 as the next choice instead of CO2. There are some serious life
safety issues you must consider when using CO2 in potentially occupied
spaces.



Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reza
Esmaeili
Sent: Thursday, August 23, 2007 10:59 AM
To: [email protected]
Subject: Re: Carbon Dioxide System Discharge Time

Jim,
I forgot to explain, the room doesn't have any operators at all, and
carbon dioxide is the best choice.
Thanks,
Reza
[EMAIL PROTECTED] wrote:
Reza:

I would not recommend a CO2 system as it is potentially too dangerous. I
would consider a clean agent sytem per NFPA 2001.

Hopefully, this is only a back-up to a wet pipe system, which is still
my favorite.

Regards,

James L.(Jim) Roberts, PE, SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)




Reza Esmaeili

Sent by: To
[EMAIL PROTECTED] [email protected]
prinkler.org cc
08/23/2007 10:18 AM
Please respond to Subject
sprinklerforum Carbon Dioxide System Discharge Time











Hi all,
For designing a total flooding high pressure carbon dioxide system in a
3,500 cubic feet computer room with electrical equipment and cable runs,
I have specified my room as "Dry electrical hazard" with flooding factor
of
0.083 lb/cubic.feet and 50% design concentration according to NFPA-12.
My questions are as below:
1)- Is a computer room fire a deep seated fire?
2)- NFPA 12 states that "For deep-seated fires, the design concentration
shall be achieved within 7 minutes, but the rate shall be not less than
that required to develop a concentration of 30 percent in 2 minutes." Is
it a problem if the total discharge time would be only 1 minute for this
case?
Many thanks for your help in advance.
Reza


---------------------------------
Pinpoint customers who are looking for what you sell.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person or entity to
which it is addressed and may contain proprietary, business-confidential
and/or privileged material.
If you are not the intended recipient of this message you are hereby
notified that any use, review, retransmission, dissemination,
distribution, reproduction or any action taken in reliance upon this
message is prohibited. If you received this in error, please contact the
sender and delete the material from any computer.

Any views expressed in this message are those of the individual sender
and may not necessarily reflect the views of the company.
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



---------------------------------
Looking for a deal? Find great prices on flights and hotels with Yahoo!
FareChase.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person or entity to
which it is addressed and may contain proprietary, business-confidential
and/or privileged material. 
If you are not the intended recipient of this message you are hereby
notified that any use, review, retransmission, dissemination,
distribution, reproduction or any action taken in reliance upon this
message is prohibited. If you received this in error, please contact the
sender and delete the material from any computer. 

Any views expressed in this message are those of the individual sender
and may not necessarily reflect the views of the company. 
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


       
---------------------------------
Building a website is a piece of cake. 
Yahoo! Small Business gives you all the tools to get online.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to