I would agree with the architect that the structure is non-combustible.
The plywood would be similar to interior finish and not part of the
structure.  The TC has ruled in the past that typical patio furniture,
including wood, plastic, and cushions are not considered sufficient
combustible loading to trigger sprinklers on all balconies.  But, you
can have extreme examples of combustible loading on a balcony where
sprinklers are needed.  The plywood does add to the overall fuel load
that could be anticipated.  Not sure if this alone pushes them over the
edge, but there is an upper limit to the amount of combustible that
should be permitted without sprinklers.

Ray Schmid, PE
Koffel Associates

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Friday, August 24, 2007 4:05 PM
To: [email protected]
Subject: combustible balconies

We have an architect arguing that NFPA 13 8.15.7 refers to the
construction
of a balcony and not the finishes. We have a non-combustible structure
with
real wood plywood attached directly to the concrete for the ceiling. I
believe there are also some boxing around the beams etc. We are saying
it
needs protection and he says it does not.

He is requesting commentary for this. Does anyone have anything I can
give
him?

Thanks,
Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to