Is there an NFPA 13 equivalent to this for dwelling units? I ran into this
on a hi-rise condo where we were trying to space our sprinklers 36" away
from ceiling mounted lights. The bathrooms were to irregular shaped and
evertime we tried to relocate the sprinkler from center of room we had
shadowing somewhere.

Thanks,

Randy Knutson
Shilo Automatic Sprinkler, Inc. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, September 05, 2007 4:30 PM
To: [email protected]
Subject: Re: Residential spray wrap-around.

look at 13R: A.6.7.7.1.5.6.  It identifies that small shadowed areas  
up to 3 sf are not a problem.  It also emphasizes that water droplets  
do not follow a linear path (like a beam of light) which jives with  
your wrap-around reference.

Roland

On Sep 5, 2007, at 12:50 PM, [EMAIL PROTECTED] wrote:

> The situation is a bathroom in a SFR that is cover by one head. Due  
> to the configuration of the room there is a very small corner that  
> is being shadowed. A pie shape shadow  from 0" to 6" wide and 2'  
> long. To place a head to cover this shadow, in my opinion, is not  
> reasonable and would be over-kill. The plan checker sites the code  
> not allowing shadowing. I am confident the operation of the single  
> head would cool the room to allow escape. The intent of 13D is  
> being met.
>
> Has anyone heard the argument (or phenomenon) of spray wrap-around  
> for these situations?
>
> Regards,
> Mike
>
> ______________________________________________________________________ 
> __
> Email and AIM finally together. You've gotta check out free AOL  
> Mail! - http://mail.aol.com
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to