Yes, gypsum directly to the bottom of the tji. Light hazard offines. It
qualifies for no sprinklers required.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of art
Sent: Friday, September 07, 2007 2:55 PM
To: [email protected]
Subject: RE: Concealed spaces

Describe the ceiling more clearly. Is there drywall attached to the bottom
of the joists of the light hazard offices?

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Friday, September 07, 2007 2:00 PM
To: AFSA
Subject: Concealed spaces

I have an all steel building (rigid rafters and z-purlins) open to the roof
deck with sprinklers at the deck. On the floor below is an "island" of
several offices with a gypsum ceiling attached to composite wood joist
topped with 3/4 " decking which forms the floor of a mezzanine above these
offices. This non-sprinklered concealed space requires of course the 3000
sq. ft. remote area in the adjacent areas. Does this mean that the system at
the roof deck 15' above this mezzanine must be calculated using the 3000
s.f. area size?

 

All input will be greatly appreciated,

Ron


Internal Virus Database is out-of-date.
Checked by AVG Free Edition. 
Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007
1:39 PM
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Internal Virus Database is out-of-date.
Checked by AVG Free Edition. 
Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007
1:39 PM
 

Internal Virus Database is out-of-date.
Checked by AVG Free Edition. 
Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007
1:39 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to