Hello Steve,

We are finishing a whole multi-purpose building here for a church, Offices, 
Kitchen, Full court plus some gym area including to portico areas outside as 
light hazard (.10). I would look at 5.2 then A5.2 in the 07 version of 13 Also 
21.36.1.1 can apply.

Saturday, September 8, 2007, 12:32:54 AM, you wrote:

> What is the consensus for classifying the hazard level of multi-purpose
> areas in churches?  I seem to remember this being discussed before but
> cannot find anything in the archives.  I am looking at a 17,000 sqft church
> with a large central sanctuary/gymnasium/multi-use area.  I would think that
> light hazard protection would be inadequate because of the probable use of
> the space for bazaars, shows, exhibits, bake sales, etc. but I'm wondering
> what the best approach is.  

>  

> Have a good weekend and thanks in advance for any help.

>  

> Steve Kowkabany, P.E.

> Fire Protection Engineer

> Neptune Fire Protection Engineering LLC

> 216 Seagate Avenue Unit B

> Neptune Beach, FL 32266

> 904-652-4200 Phone

> 904-212-0868 Fax 

>  

>  

>  

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)



-- 
Best regards,
Charles Thurston 
 Coastal                            mailto:[EMAIL PROTECTED]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to