To add to Greg's post, the only thing I have seen that might question the LH designation is any rummage or clothing sales. If this is an issue, perhaps they could pick a room for this and bump the protection up in that area.

Encapsulated cranberry-nut bread in the quantities usually present would not be a significant problem.


At 07:45 AM 9/10/2007, you wrote:
In my experience, most churches do not use their multi-purpose areas like
secular buildings would. They typically do no have car shows, gun shows and
exhibits like buildings which rent out by the day or week might.

I certainly would not consider a church bake sale "mercantile" based on the
low quantities of goods and the lack of permanent displays.

I would consider most if not all of them Light Hazard without much question.
Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Coastal
Sent: Saturday, September 08, 2007 8:27 AM
To: Steve Kowkabany
Subject: Re: Church Multi-Purpose Areas

Hello Steve,

We are finishing a whole multi-purpose building here for a church, Offices,
Kitchen, Full court plus some gym area including to portico areas outside as
light hazard (.10). I would look at 5.2 then A5.2 in the 07 version of 13
Also 21.36.1.1 can apply.

Saturday, September 8, 2007, 12:32:54 AM, you wrote:

> What is the consensus for classifying the hazard level of multi-purpose
> areas in churches?  I seem to remember this being discussed before but
> cannot find anything in the archives.  I am looking at a 17,000 sqft
church
> with a large central sanctuary/gymnasium/multi-use area.  I would think
that
> light hazard protection would be inadequate because of the probable use of
> the space for bazaars, shows, exhibits, bake sales, etc. but I'm wondering
> what the best approach is.

>

> Have a good weekend and thanks in advance for any help.

>

> Steve Kowkabany, P.E.

> Fire Protection Engineer

> Neptune Fire Protection Engineering LLC

> 216 Seagate Avenue Unit B

> Neptune Beach, FL 32266

> 904-652-4200 Phone

> 904-212-0868 Fax

>

>

>

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)



--
Best regards,
Charles Thurston
 Coastal                            mailto:[EMAIL PROTECTED]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to