NFPA Standards require the use of LISTED fire protection equipment.  
Mechanics aside, if it isn't listed, it doesn't meet NFPA Standards.
 
Forest Wilson
Cherokee Fire
 
 
 
 
In a message dated 9/8/2007 11:10:23 A.M. Eastern Daylight Time,  
[EMAIL PROTECTED] writes:

On  9/8/07, Reza Esmaeili <[EMAIL PROTECTED]> wrote:
> Hi  All,
>   How much a fire pump efficiency is  important?
>   When want to buy an agriculture pump which  should work at least 12 hours 
a day, then efficiency is very important to  decrease energy cost. But a fire 
pump which may work totally 50 hours/Year and  energy saving is not a matter 
of importance for a fire pump, why shoild I buy  high efficiency fire pumps.
>   I think even a low  efficiency(Ex. 60%) fire pump which meets NFPA 
standards (Deliver not less  than 65 percent of rated head at 150 percent of 
rated 
capacity) can be a good  choice and no need to spend too much money to buy high 
efficiency (Ex. 90%)  fire pump.
>   I believe that even a low efficiency fire pump  is as reliable as a high 
efficiency fire pump for fire  protection.
>   What do you think about  it?
>   Thanks,
>    Reza


 