Reza:

1 - You can put as many sprinklers on a grid that you can hydraulically
prove.  You can put as many on a tree as you can hydraulically prove. 

2 - I am not sure I understand you here.  You aren't required to place
sprinklers directly on the main.  It is may not be a good idea because you
likely have to sprig the head.

3 - Pipe sizing is based on hydraulic calculations.  The mains may or may
not be the same size.
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reza Esmaeili
Sent: Sunday, September 09, 2007 2:51 PM
To: [email protected]
Subject: Sprinkler Gridded Systems

Hi!
  I have some questions about sprinkler gridded systems, thanks for your
attention in advance.
  1- Is there any limitation in number of sprinklers to place on each branch
of a wet pipe sprinkler gridded system? Can I put 25 sprinklers on each
branch while I am hydraulically calculate the most remote area?
   
  2- In gridded systems, there are sprinklers on one of the cross main, am I
allowed if I don't place sprinklers on none of the cross mains? (No
sprinkles on cross mains)
   
  3- Do both cross mains have the same size?
   
  Thanks,
  Reza
   
   
   
   

       
---------------------------------
Need a vacation? Get great deals to amazing places on Yahoo! Travel. 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

__________ NOD32 2516 (20070909) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to