We just looked at something similar yesterday AM, and #13-2002 8.6.6 was
pretty clear about just maintaining 18" clear below the deflector being
adequate. The 3x rule started getting into the 6-deep cross-referenced rules
where my eyes glazed over and we already had our answer. But you're half-way
there!

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Tuesday, September 11, 2007 7:19 AM
To: [email protected]
Subject: Floor-mounted vertical obstruction

I am not sure if this got up to the list yesterday so I am sending it again.
It is odd that there was no response, any input would be appreciated.

________________________________

From: Dewayne Martinez
Sent: Monday, September 10, 2007 11:23 AM
To: '[email protected]'
Subject: Floor-mounted vertical obstruction


We are bidding a self storage building that will have partial height
walls (5ft on center) to 2ft below the deck with chain link fence to the
deck.  This will be designed to an OH II density so the rules for
floor-mounted vertical obstructions will not apply since they are for
light hazard only.   If we can arrange it so that the wall is more 18in
below the sprinkler deflector can we ignore them per 8.6.5.3 (13
(o7ed))?  If the top of the wall is closer that 18in to the deflector do
we follow 3 times rule?  Thanks for your input in advance.
Dewayne Martinez, CET
Design Build Fire Protection
[EMAIL PROTECTED]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to