We fit all the criteria re ceiling pockets to eliminate the sprinklers on a 
condo project except the local AHJ decided the wood glued to the drywall 
ceiling in the pocket created a combustible space which required sprinklers.  
Only meant an additional 20 or so sprinklers in an elevator lobby corridor so 
that we might protect the decorative ceiling with the pendent sprinklers.  I 
want to retire.

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Tuesday, September 11, 2007 10:32 AM
To: [email protected]
Subject: RE: 8.6.7 Ceiling Pockets

Ed, A new guy here put a sprinkler in each skylight and I challenged him
on why. He pointed to 8.6.7 and asked if they could be omitted where it
said that. Damned if I could find anything in 13.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Tuesday, September 11, 2007 7:19 AM
To: [email protected]
Subject: RE: 8.6.7 Ceiling Pockets

Ron, if my memory hasn't completely gone, I remember a discussion that
essentially said you could have multiple skylights with less than 10'
separation and treat them as a single skylight providing the aggregate
volume was less than 1000 cf.  Does this ring a bell with anybody else?


Ed Kramer
Littleton, CO


>Five 2 ft. x 2 ft. X 2 ft. Skylights located in a row each with 2 ft.
>separation from the next. Does 8.6.7.1 require each skylight have to
>have a head because they are not separated by at least 10 ft?
>
>Ron Fletcher
>Aero Automatic Sprinkler
>Phoenix, AZ
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to