Is the space above the mezzanine protected by the ESFR system?  What is
the space above the platform being used for?

The area adjacent to the mezzanine is protected with ESFR sprinklers,
what is this system protecting?  

If it is storage, what is the height and the commodity?


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jimmy
Waite
Sent: Wednesday, September 19, 2007 3:25 PM
To: [email protected]
Subject: Mezzanine/ ESFR 

Hello all again,

 

Apparently the thing to do out west is to add mezzanines years after the
original building is built, and then sprinkle them after you get
caught/get in trouble.  We have a job that is a warehouse designed with
and ESFR system.  The owner has since come in and built a mezzanine.
The mezzanine is roughly 67' by 33.5' and is about 9'-10 tall.  The
mezzanine is located on an exterior wall, and the warehouse is 30' tall
at the peak.  There is no separation around the exterior of the
mezzanine.

 

Now that I have explained the space, let me explain the scenario.  The
space under the mezzanine is used to pull orders.  They keep the
merchandise in plastic totes while it is under the mezzanine.  So all
the storage is transient.  The totes sit in a flow through racks, to
hold orders before they go to a truck, that doesn't store above 5'.  

 

Now to my question.  Now the standard seems to be pretty clear, that
since there is no separation, the '07 in sections 11.1.2 (1) and 12.3
(1) say that since there is no separation the hazard needs to be carried
15'-0 beyond the hazard perimeter.  Do these sections apply to both
above and below the mezzanine?  Would I have to carry the ESFR design
criteria 15' into the mezzanine floor area?  This seems a bit much
considering the space would normally be misc. storage in the'07.  But I
also can see the justification to increase the design criteria since the
mezzanine is surrounded on three sides by storage.

 

If ESFR is required I know I'll have several problems.  I won't have the
clearance needed between the deflector and storage.  Also, the mezzanine
is non-combustible Obstructed construction.  Would there be any other
design criteria I could use, other than ESFR?

 

I've never done an ESFR system before and definitely need the help.  I
have pictures that could clarify what I'm talking about if anyone would
like them that I willing to give some suggestions.

 

 

Jimmy Waite

Burtell Fire Protection, Inc.

[EMAIL PROTECTED]

(406) 652-7697

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to