Hello all again,

 

Apparently the thing to do out west is to add mezzanines years after the
original building is built, and then sprinkle them after you get caught/get
in trouble.  We have a job that is a warehouse designed with and ESFR
system.  The owner has since come in and built a mezzanine.  The mezzanine
is roughly 67' by 33.5' and is about 9'-10 tall.  The mezzanine is located
on an exterior wall, and the warehouse is 30' tall at the peak.  There is no
separation around the exterior of the mezzanine.

 

Now that I have explained the space, let me explain the scenario.  The space
under the mezzanine is used to pull orders.  They keep the merchandise in
plastic totes while it is under the mezzanine.  So all the storage is
transient.  The totes sit in a flow through racks, to hold orders before
they go to a truck, that doesn't store above 5'.  

 

Now to my question.  Now the standard seems to be pretty clear, that since
there is no separation, the '07 in sections 11.1.2 (1) and 12.3 (1) say that
since there is no separation the hazard needs to be carried 15'-0 beyond the
hazard perimeter.  Do these sections apply to both above and below the
mezzanine?  Would I have to carry the ESFR design criteria 15' into the
mezzanine floor area?  This seems a bit much considering the space would
normally be misc. storage in the'07.  But I also can see the justification
to increase the design criteria since the mezzanine is surrounded on three
sides by storage.

 

If ESFR is required I know I'll have several problems.  I won't have the
clearance needed between the deflector and storage.  Also, the mezzanine is
non-combustible Obstructed construction.  Would there be any other design
criteria I could use, other than ESFR?

 

I've never done an ESFR system before and definitely need the help.  I have
pictures that could clarify what I'm talking about if anyone would like them
that I willing to give some suggestions.

 

 

Jimmy Waite

Burtell Fire Protection, Inc.

[EMAIL PROTECTED]

(406) 652-7697

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to