I am working on an installation (NFPA 13) where the only water supply is from a small pump taking suction from 2 -5000 gallon tanks. There is no by-pass on the system as the flow from the tanks without the pump is of no value. We have two systems, a wet and a dry. The FDC is fed below the risers. The question came up from the contractor if the two control valves on the risers can be considered the discharge valve for the fire pump. My contention is that if the valves are shut down to work on the pump, no water could be pumped in through the FDC. The contractor's arguement is that the check valve on the discharge will allow a satisfactory stop to allow the control to remain open while the pump is out of service. I don't buy into that. If that were the case, then why require a discharge control valve at all? Unfortunately, both the diagrams in NFPA 20 and the diagram in NFPA 13 section 8.15.1.1 are in the appendix, which are not part of the standard, which the contractor states are only suggestions. Am I right or am I once again over-engineering something?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com