Todd,

I think I agree with you.  It's difficult at times to envision what we try
to describe in our posts.  If I understand what you have described, it
sounds like an additional control valve is needed after the discharge of the
pump and before the FDC connection.  I would not accept a system that is
left completely out of commission while maintenance is being done on the
pump.

Cliff Whitfield
Fire Design, Inc.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of FPDC
Sent: Tuesday, September 25, 2007 2:25 PM
To: [email protected]
Subject: pump discharge valve.

I am working on an installation (NFPA 13) where the only water supply 
is from a small pump taking suction from 2 -5000 gallon tanks. There 
is no by-pass on the system as the flow from the tanks without the 
pump is of no value. We have two systems, a wet and a dry. The FDC is 
fed below the risers. The question came up from the contractor if the 
two control valves on the risers can be considered the discharge 
valve for the fire pump. My contention is that if the valves are shut 
down to work on the pump, no water could be pumped in through the 
FDC. The contractor's arguement is that the check valve on the 
discharge will allow a satisfactory stop to allow the control to 
remain open while the pump is out of service. I don't buy into that. 
If that were the case, then why require a discharge control valve at 
all? Unfortunately, both the diagrams in NFPA 20 and the diagram in 
NFPA 13 section 8.15.1.1 are in the appendix, which are not part of 
the standard, which the contractor states are only suggestions. Am I 
right or am I once again over-engineering something?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to