Remember to consider 20 psig at the sprinkler
if the spacing perpendicular to the slope is > 8 ft.
This applies to SSP & SSU.  2007 nfpa Table 8.6.2.2.1(a).


Which brings up a question:

besides the listed "attic sprinkler" and SSP´s and SSU´s...
what OTHER sprinklers are approved for use in sloped attics?

Would residential sprinklers listed for beamed ceilings with pitches
up to 8 in 12 be approved for attics?

scot deal
excelsior fire engineering