We saw quite a wide array of what are 13R fire pumps, and what are (almost)
13R fire pumps at the AFSA convention trade show.

We have a project with 30 or 40 of these, and are preparing a variance
request for the local AHJ since we don't believe 30 minutes of stored water
is needed with a paid city FD with stations 4 and 10 blocks from our sites.

What has been the acceptance rate of the lightweight pumps that aren't
listed fire pumps in accordance with NFPA #20, but require specific approval
of the local AHJ?

Are most of you installing the pseudo-pumps or the real pumps?

Did y'all know there was a difference, and that some
manufacturers/assemblers aren't all that clear on their semi-compliance?