We saw quite a wide array of what are 13R fire pumps, and what are (almost) 13R fire pumps at the AFSA convention trade show.
We have a project with 30 or 40 of these, and are preparing a variance request for the local AHJ since we don't believe 30 minutes of stored water is needed with a paid city FD with stations 4 and 10 blocks from our sites. What has been the acceptance rate of the lightweight pumps that aren't listed fire pumps in accordance with NFPA #20, but require specific approval of the local AHJ? Are most of you installing the pseudo-pumps or the real pumps? Did y'all know there was a difference, and that some manufacturers/assemblers aren't all that clear on their semi-compliance? George Church Rowe Sprinkler _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)