Forum, The following from the Annex "A.8.16.2.5.2.1 An example of an accessible location would be a valve located approximately 7 ft (2 m) above the floor level to which a hose could be connected to discharge the water in an acceptable manner." indicates that a drain valve would be "accessible" if it was located 7 feet above the floor level.
8.17.4.2.2 states that "The test connection valve shall be readily accessible. " 8.17.4.3.2 states that "The trip test connection shall be located on the end of the most distant sprinkler pipe in the upper story and shall be equipped with a readily accessible shutoff valve and plug not less than 1 in. (25 mm), at least one of which shall be brass." 8.17.4.4.4 states that "For double interlock preaction systems in excess of 750 gal (2840 L), the trip test connection shall be located on the end of the most distant sprinkler pipe in the upper story and shall be equipped with a readily accessible shutoff valve and plug not less than 1 in. (25 mm), at least one of which shall be brass." And finally, 8.16.1.1.7 states that "Control Valve Accessibility. All control valves shall be located where readily accessible and free of obstructions." My question is what is the difference between "accessible" and "readily accessible"? I have a computer room that requires a separate control valve for it and I contend that for it to be readily accessible, it must be unobstructed and within reach by a person from the floor without resorting to use of a ladder. I also contend that readily accessible does not allow the control valve to be installed above a layin ceiling. The only NFPA Standard with a definition is the NEC. It states "Accessible, Readily (Readily Accessible). Capable of being reached quickly for operation, renewal, or inspections without requiring those to whom ready access is requisite to climb over or remove obstacles or to resort to portable ladders, and so forth. Therefore, I believe that the valve must be installed on the wall of the computer room and not above the layin ceiling. What say you all? Thank You Rahe Loftin, P.E. Region 7 - GSA Office - 817-978-7299 Fax - 817-978-8644 Cell - 817-371-3102 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)