Forum,
The following from the Annex "A.8.16.2.5.2.1  An example of an accessible
location would be a valve located approximately 7 ft (2 m) above the floor
level to which a hose could be connected to discharge the water in an
acceptable manner." indicates that a drain valve would be "accessible" if
it was located 7 feet above the floor level.

8.17.4.2.2 states that "The test connection valve shall be readily
accessible. "

8.17.4.3.2 states that "The trip test connection shall be located on the
end of the most distant sprinkler pipe in the upper story and shall be
equipped with a readily accessible shutoff valve and plug not less than 1
in. (25 mm), at least one of which shall be brass."

8.17.4.4.4 states that "For double interlock preaction systems in excess of
750 gal (2840 L), the trip test connection shall be located on the end of
the most distant sprinkler pipe in the upper story and shall be equipped
with a readily accessible shutoff valve and plug not less than 1 in. (25
mm), at least one of which shall be brass."

And finally, 8.16.1.1.7 states that "Control Valve Accessibility. All
control valves shall be located where readily accessible and free of
obstructions."

My question is what is the difference between "accessible" and "readily
accessible"?  I have a computer room that requires a separate control valve
for it and I contend that for it to be readily accessible, it must be
unobstructed and within reach by a person from the floor without resorting
to use of a ladder.  I also contend that readily accessible does not allow
the control valve to be installed above a layin ceiling.

The only NFPA Standard with a definition is the NEC.  It states
"Accessible, Readily (Readily Accessible). Capable of being reached quickly
for operation, renewal, or inspections without requiring those to whom
ready access is requisite to climb over or remove obstacles or to resort to
portable ladders, and so forth.

Therefore, I believe that the valve must be installed on the wall of the
computer room and not above the layin ceiling.

What say you all?

Thank You

Rahe Loftin, P.E.
Region 7 - GSA
Office - 817-978-7299
Fax - 817-978-8644
Cell - 817-371-3102


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to